Dear Environs,Can any one help me out what are the permissions required for installing new D. G set in a hospital.Is there any permissions need to be taken from Andhra Pradesh pollution Control board.Since the Hospital already using one D.G Set.

You need to be a member of Paryavaran.com- Indian Environment Network to add comments!

Join Paryavaran.com- Indian Environment Network

Email me when people reply –

Replies

  • https://docs.google.com/open?id=0B3b7IOMMivK2UlExaEhZR3FTOXFHOVVFbF...

    here is link to download green book 

  • sir,
    what is the green book. where can i get that.
    thanking you sir
  • Both consent to operate and consent to operate is required from state board.Refer green book

    Dr B N das

  • Thank you for the information sir
  • Dear,

    Yes, you would require CTE (consent to establish) for new DG set installation ( capacity more than 15 KVA in case non industry.. but u need to confirm) & CTO (consent to operate)from the APPCB under Section 21 of the Air (Prevention & Control of Pollution) Act, 1981 as amended. 

    For rest of the requirement check the below given link.

    http://www.cpcb.nic.in/Generator.php

  • yes you need to aaply for varied consent to operate . 

    and D.G set should be with canopy or an acoustic room  should be provided for a D.G set 

    also their are parameters for the stack height of the exhaust of D.G set .

    generally it should me more than 3m meters from roof level if D.G set's capacity is below 500kva i guess .